Barry1961
Industrial
- Oct 3, 2003
- 530
A customer has a 10 hp, 480 V, 3 ph, Baldor Motor # CWDM3714T driving a mixer through a 100:1 helical gearbox. The motor is being driven by a WEG VFD in the volts/hertz mode, (not vector) at 25 Hz. The following reading were taken by a old clamp on amp/volt meter, Simpson I think, which does not have very fine scale for reading voltage. The PWM carrier frequency is 5 khz.
The customer is going to change the ratio to run the motor at 60 hz after testing and wants to calculate how much torque he is really using. He is getting someone to fix the unbalanced incoming line.
The load is pulsing at about 1 hz which is reflected in the amp draw.
Line coming to VFD
Voltage from phase to phase, 480 V, 480 V, 460 V
Current, 6 A, 6 A, 3 A
Motor Leads, Motor is rated at 13.5 amp
5 to7 amp pulse, balanced
VFD current display
13 to 15 amp pulse
Which reading can I believe to calculate torque at 25 hertz?
Do I need to get another amp meter to read the 5khz carrier?
Will the unbalanced line affect this besides heating up the buss diodes?
Baldor Motor Data
7.8 A at 25% FLT
9.2 A at 50% FLT
11 A at 75% FLT
13.5 A at 100% FLT
16.2 A at 125% FLT
Thanks!!!
Barry1961
The customer is going to change the ratio to run the motor at 60 hz after testing and wants to calculate how much torque he is really using. He is getting someone to fix the unbalanced incoming line.
The load is pulsing at about 1 hz which is reflected in the amp draw.
Line coming to VFD
Voltage from phase to phase, 480 V, 480 V, 460 V
Current, 6 A, 6 A, 3 A
Motor Leads, Motor is rated at 13.5 amp
5 to7 amp pulse, balanced
VFD current display
13 to 15 amp pulse
Which reading can I believe to calculate torque at 25 hertz?
Do I need to get another amp meter to read the 5khz carrier?
Will the unbalanced line affect this besides heating up the buss diodes?
Baldor Motor Data
7.8 A at 25% FLT
9.2 A at 50% FLT
11 A at 75% FLT
13.5 A at 100% FLT
16.2 A at 125% FLT
Thanks!!!
Barry1961