Lewist57,
You can analyze existing systems the same manner as "new" systems. Caesar doesn't know (or doesn't care) if the system being analyzed is in a construction stage or existing pipe in 100 years old plant.
One foot displacement seems too big. What pipe size we are talking about? What are spans to next supports, type of supports and fluid inside the pipe.
I think main issue here could be supports were not adequately designed to carry all loading conditions at first place.
Is it someone saw piping moved 1 foot during operations and broke the pipe or it is after the fact when it have broken they measured that the pipe sag 1 foot.
It is not necessarily pipe broke right after hanger was gone. In many instances pipe hangers brake due to water/steam hammer, vibration, earthquake, wind, snow, ice and other loading conditions. It remain undetected or neglected by operations and pipe become to subject to shaking or vibration which over time (many month or even years) brakes the pipe. You can see that by investigating pipe cracks, because fatigue cracks are different then ultimate, corrosion, or brittle fracture.
OK. What is now? A pipe is broke and have to be fixed. What are steps need to be taken?
1. Examine cracks, nearby supports (they could be broken too) and find out what was the main contributor to the pipe failure.
2. Analyze whole pipe line from one end to the other for piping stress for current layout and supports. Consider all operational, upset, occasional conditions.
3. Design new supports and/or layout based on #1 and 2.
There is so much you can do. That's what should be done in those circumstances, IMHO.
Regards,
Curtis