I am working on a 300 HP VFD application, running a pump. The breaker upstream of the VFD is 500A. The drive is rated at 385A. The question I have is about cable sizing. My motor nameplate is 330A, and following NEC I can use 2 runs of 4/0, with #2 for a ground wire. If I use 90C cable, derated for 6 cables in a conduit, I get 125% of the motor nameplate, and I'm allowed to use the nameplate instead of the table because this is a variable speed motor.
I normally size the conductors based on NEC, not based on the drive manufacturer recommendations. This time I checked, and the Eaton manual says for power wiring to use 2 runs of #300 with a #300 ground wire. They recommend 75C wire.
Eaton is two sizes above me with the current carrying conductors, and they are exceptionally oversized with respect to the ground. This is so far different from my calculations that now I'm concerned about why they would recommend this.
Has anyone experienced this? Any ideas?
EE
EE