Hello,
I have a question regarding instrument cable. I know that for 4-20ma transmitters twisted pair cable should be used with the screen grounded at one end only. However for digital signals ( limit switches , push buttons ) can 2 core/ part of a multi core cable be used ?

Thanks
 
Yes as long as you only use the parts for 24 VDC and don't mix them with AC Voltage.

BR A

“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
 