Gents
Folowing a 240mm2 3c 3.3kV cable failure i have been taksed with replacing the cabling of the circuit that experienced the fault. The cables (3 parallel 3c 240mm2 XLPE) run from an incoming 3.5MVA transformer to our 3.3kV Motor Control Centre for a run of approx 50m, with around 30 direct buried and the last 20 in buried single way ducts. Other cables run along the same path but budget will not be approved for the replacement of these.
I have been tasked with looking at installing the new cables on ladder racking, which will allow only the damaged cicuit to be replaced with the existing healthy cables left in situ, but have been advised not to bring the cables above ground by colleagues.
They haven't given any tangible arguments that I can go back to the site owners with so I was hoping someone on here may be able to provide some assistance and guidance on the risks, as seen by the industry, that are posed by above ground MV cabling.
Co-incidentally I believe ladder racking will be fine on this site and due to the available route will cause no access issues.
Any thoughts?
Folowing a 240mm2 3c 3.3kV cable failure i have been taksed with replacing the cabling of the circuit that experienced the fault. The cables (3 parallel 3c 240mm2 XLPE) run from an incoming 3.5MVA transformer to our 3.3kV Motor Control Centre for a run of approx 50m, with around 30 direct buried and the last 20 in buried single way ducts. Other cables run along the same path but budget will not be approved for the replacement of these.
I have been tasked with looking at installing the new cables on ladder racking, which will allow only the damaged cicuit to be replaced with the existing healthy cables left in situ, but have been advised not to bring the cables above ground by colleagues.
They haven't given any tangible arguments that I can go back to the site owners with so I was hoping someone on here may be able to provide some assistance and guidance on the risks, as seen by the industry, that are posed by above ground MV cabling.
Co-incidentally I believe ladder racking will be fine on this site and due to the available route will cause no access issues.
Any thoughts?