Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

C Value 2" Flexible Hose 1

Status
Not open for further replies.

cr1973

Civil/Environmental
Joined
Jul 30, 2003
Messages
100
Location
US
Anyone know the C values for 1" rubber hose, or 2" and 3" flexible hosing, commonly used on hydrant outlets?

I've been assuming 90 or 100.
 
Typical values of c for commonly used rubber-lined hoses are as follows:

Hose diameter c value
1" 150
1-1/2" 24
2" 8

The values of c for various hoses, can be found in the Fire Protection Handbook published by the National Fire Protection Association (NFPA).
 
Note the NFPA equation the c bimr gave is not the H-W equation. So the NFPA c does not equal the C in the H-W equation, if that is what you wanted.

Engineering is the practice of the art of science - Steve
 
Sorry, I should have been more clear - I am looking for the Hazen Williams C value.

Anyone have a rough idea, am I pretty close using a c of 100?
 
C=100 for rubber hose is probably a conservative value and hardly think that anyone would second guess you for that.
 
I have seen values of 130 that correspond with manufacturer friction loss tables, a little higher than probably occurs with an older hose.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top