medeek
Structural
- Mar 16, 2013
- 1,104
As I'm going through the "Guide to the Wind Load Provisions of ASCE 7-10" by Mehta and Coulborne I noticed an inconsistency with the regard to the way the effective area for a roof panel is determined. In the one example the roof panel is a 4x8 plywood panel on 24" o/c spaced trusses with the eff. area given as 32 ft2. On the other example the roof panel is 2x8 spanning across trusses that are 48" o/c with the eff. area given as the larger of 4 x 2 = 8ft2 or (4*4)/3 = 5.3 ft2.
If the 4x8 sheet of plywood is spanning the trusses with the long axis perpendicular to the trusses (case 1) shouldn't the span then be 2 ft. The effective area would be the larger of either 2x4 = 8 ft2 or (2*2)/3 = 1.33 ft2.
When dealing with windows, doors and roof panels do you consider the actual area of the component or consider some spanning distance and then compare this distance squared divided by 3 to the trib area? I guess what to use as the effective area for some components had got me a little confused.
If the 4x8 sheet of plywood is spanning the trusses with the long axis perpendicular to the trusses (case 1) shouldn't the span then be 2 ft. The effective area would be the larger of either 2x4 = 8 ft2 or (2*2)/3 = 1.33 ft2.
When dealing with windows, doors and roof panels do you consider the actual area of the component or consider some spanning distance and then compare this distance squared divided by 3 to the trib area? I guess what to use as the effective area for some components had got me a little confused.