KootK said:
a) You've got ample thrust resistance everywhere (no end span).
If there are concrete piers at the end of the wall, why couldn't it resist lateral loads and provide siffness? Concrete should be significantly stiffer (probably around 20 times) than stone masonry.
KootK said:
b) You've got enough arch depth that you can keep everything in compression always and not rely on tensile or shear stresses (L/10 is not that in my book).
Everything in compression seems too strict for an arch that supports lateral loads, or any URM element. This would mean that no cracks are allowed to form, most books I've read on URM seem to rely on plastic failure mechanism, i.e. finding an arch that "fits" inside the wall, this is very different than everything being in compression.
For example, let's look at a simple wall under vertical load with some out of plane eccentricity. If you want everything to be in compression you need to limit the total eccentricity to t/6. If you allow the stress block to be 10 % of the wall thickness you get an allowable eccentricity of 0,45*t - that is 2,7 times more! Of course, you get a lower axial capacity, but that is usually quite high for standard dimensions.
This arch action is not that high, you get relatively low capacities, but still... it's not zero. Additionally it does span in the opposite direction as well which helps a bit.
What would happen if instead of a 20" stone wall that is cracked you had a 2" thick stone arch that is fully in compression? If you can make sure that this arch is fully in compression that is lower than strength, what is the problem?
KootK said:
c) You've got enough load symmetry that you can keep everything in compression always an not have to consider arch buckling (not plausible with soil load in my book).
How do you consider this non symmetry? Since we're talking about a horizontal arch it should a a horizontal non symmetry. You could still fit an arch of t/10 in there, the ultimate load will be lower depending on the level of symmetry. That is why you do calculations. I have never seen soil non symmetry in a horizontal plane though.
Don't get me wrong, I would also rather have reinforcement in my elements that can resist tension, but if 80 % of buildings in your city (and country... and continent) are over 100 years old with URM basements and they survived without damage a few significant earthquakes you just can't afford to say that it's not good if there is a rational model for it.
Sure, it seems wise to design URM in a way that it is not very close to failure, so I'd deffinitely space the buttresses closer together rather than far apart.
I quite like The Stone Skeleton, "Guastavino vaulting" also seems like an interesting read, I think he did some vaults in the US.