@Waross.
Thank you for the advice. I will look at the voltage drop applicable, but my application is using bars for a length of about 10 feet.
I will also precise that it is for a machine (enclosure), and that I was planning on using Flexibars by NVent (Eriflex). Those have insulation. In their manual, they precise that mounted on edge, two run in parallel (no distance stated obviously), the ampacity of two is 1.72 times the ampacity of one. With three, 2.25 times that.
I had one question for them, which was at which distance from each other that derating would apply and they were very unhelpful. Here it is:
"The ampacity derating coefficient is used to help determine the size and quantity of Flexibar needed. We have not evaluated at different separation distances and cannot provide guidance on this question.
Each application is different, so the best way to evaluate the temperature rise of one or more Flexibar in parallel is to install Flexibar into the panel and monitor the temperature rise."
This is why I resorted to ask here in order to know what is done when using rigid busbars, which is probably more commonplace.
For my application, where I should in theory provide conductors of 900A (to be 1.25 times above FLA) without much restriction in terms of heat, Flexibars with 5 laminations of 63mm high would get me an ampacity of 883A at a delta T of 30C, according to their table.
Since I will run three in parallel (ONE per phase), if I am applying the 2.25 factor, I need a set of Flexibars of 10 laminations of 100mm high (over 1900A at same Delta T). It's quite a difference for mounting, space, etc.
I want to do it right, but not overdo it necessarily. I can place the bars (they are insulated by the way) a minimum of 1/2" from each other and possibly widen that to 1 inch.
I hope this information helps in solving my issue.