Curtain walls are required to withstand the lateral story drift of the building. The ultimate limit state is the glass in the curtain wall can not fall out. ASCE 7-10 13.5.9.1 requires Δfallout ≥ 1.25 * Ie * Dp
Therefore, the curtain wall needs to accommodate 1.25, 1.56, and 1.875 times the design drift of the building structure for risk categories I/II, III, and IV respectively. I understand the design drift is divided by Ie, so Ie in the Δfallout calc is not redundant. But the values seem rather high, particularly when computing the actual drift values, ex. a 15ft story height gives ~4in.+ of drift. So for those knowledgeable with buildings in seismic zones, here are a couple questions:
- Is it typical to design a structure right to those limits? Reason being most curtain wall systems are tested to H/100 (for serviceability - ie. remain air/water tight), and H/66 (for ultimate - glass can't fall out). These are recommended values from architectural test methods (ex. AAMA 501.4), and apparently not very close to the upper code limits.
- How does the drift impact other structural parts of the building, and in checking those other parts, do you include the importance factor and an additional 1.25 factor (or similar)? For example, structural separation calcs in ASCE 7-10 12.12.3 remove the importance factor, and do not have an additional 1.25 factor. So this analysis does not align with the Δfallout analysis. As a note, the 1.25 factor comes from the recommendation that drift calcs can be underestimated by up to 30% (from 6.2.10.1 in NEHRP 2000, which is referenced in the ASCE 7-10 commentary for 13.5.9.1).
- Do you ever consider seismic events at a service level? If a small earthquake hits, how is structural integrity of the building structure verified? I've yet to see wind drift values exceed H/100, so having a curtain wall system that remains air/water tight at H/100 seems pretty arbitrary.
Therefore, the curtain wall needs to accommodate 1.25, 1.56, and 1.875 times the design drift of the building structure for risk categories I/II, III, and IV respectively. I understand the design drift is divided by Ie, so Ie in the Δfallout calc is not redundant. But the values seem rather high, particularly when computing the actual drift values, ex. a 15ft story height gives ~4in.+ of drift. So for those knowledgeable with buildings in seismic zones, here are a couple questions:
- Is it typical to design a structure right to those limits? Reason being most curtain wall systems are tested to H/100 (for serviceability - ie. remain air/water tight), and H/66 (for ultimate - glass can't fall out). These are recommended values from architectural test methods (ex. AAMA 501.4), and apparently not very close to the upper code limits.
- How does the drift impact other structural parts of the building, and in checking those other parts, do you include the importance factor and an additional 1.25 factor (or similar)? For example, structural separation calcs in ASCE 7-10 12.12.3 remove the importance factor, and do not have an additional 1.25 factor. So this analysis does not align with the Δfallout analysis. As a note, the 1.25 factor comes from the recommendation that drift calcs can be underestimated by up to 30% (from 6.2.10.1 in NEHRP 2000, which is referenced in the ASCE 7-10 commentary for 13.5.9.1).
- Do you ever consider seismic events at a service level? If a small earthquake hits, how is structural integrity of the building structure verified? I've yet to see wind drift values exceed H/100, so having a curtain wall system that remains air/water tight at H/100 seems pretty arbitrary.