I have a situation where I need to buck voltage of 240-245V down to as close to 200V as possible. 200V is not a common voltage in the US so 208V may have to do. I have a couple single phase dry transformers and was considering configuring in a 3P bucking arrangement. I had to look at the diagrams to ensure there is no way a transformer failure could ever revert back to full 240V going to the equipment.
Does anyone see issue with this or pros/cons of this less expensive setup compared to an isolation set?
I am having to take a refresher on the math but as I recall, the KVA capacity in buck/boost is the voltage ratio * transformer KVA? So a 2KVA transformer operated in bucking at 32V buck would be 240/32 = 7.5 * 2kva 15kva capacity?
Is there any concerns with the delta primary side? All loads are L-L anyway so L-N are not an issue.
I was also curious of overloading capacity of this configuration for transient current draw for motor accelerations on VFDs?