Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

BTU/hr Calc for cooling a plant case?

Status
Not open for further replies.

Klankster

Computer
Joined
Jun 9, 2004
Messages
1
Location
US
I need help computing the BTU/hr required to cool a closed orchid case, and was wondering if someone here can help.

The case is roughly 42 cu. ft., 7 feet long x 2 feet wide x 3 feet high. It is lit by a 400W metal-halide light with a reflector suspended about 2" over the case, shining down into it through glass panels. Pretty much all the light goes into the case. This is the only source of heat other than ambient room temperature, which can rise to the mid-80's F.

I'm trying to determine what size cooling unit I need, and am looking at some Melcor thermoelectric units (such as their MAA070T, see These come in various sizes from 50-1200 BTU/hr. When the ambient temperature is, say, 85F and the light is on, I want to be able to hold the interior of the case to 72F.

I'm hoping someone here can give me a ballpark computation for the unit size that will do the trick, or point me in the right direction. Thanks!

-Tom
 
The calculation method is exactly the same as for a building cooling load. You should find examples in any engineering handbook. You will need to know the thermal conductivity of each wall of the case.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top