Breather valve replacing Frangible Joint

Status
Not open for further replies.

zacharialamsyah

Chemical
Joined
Nov 26, 2013
Messages
54
Location
ID
Dear All

I having some problem in facility about storage tank

Can Breather valve per API-2000 (Venting Atmospheric and Low-pressure Storage Tanks) replace the requirement of Frangible roof to shell Joint. If the construction of Frangible Joint cannot applicable per API-650 .

Thank you for your responses and answers

Regards
Zachari Alamsyah

 
A suitably sized pressure (or pressure/vacuum) relief vent per the requirements of API 2000 for emergency venting can replace a frangible roof joint. Be sure to advise your client of all pertinent information related to the vent. Reference 5.8.5.3 of API 650.
 
'Breather Valve' will have to be quite large. Look at an 'Emergency Vent' installed in the roof manway. Easy way to achieve the required diameter.
 