Marks1080 said:Mbrooke, I may be making a poor assumption but basically you want a double breaker double bus station?
I don't see why any special considerations need to be made for breaker control outside of a breaker and a half station.
If this is so, the only thing I really see you gaining is cost. Unless there's a very special customer connected I wouldn't go down this road. It seem like one of the consequences you have for trying to minimize the impact of a failed breaker is adding more breakers, which can then fail.
In my opinion the decreased security doesn't justify the cost of an incremental increase of reliability.
David Beach said:Agreed, I wouldn't call yours as breaker and a third since there isn't a third position in there. Breaker and a half doesn't require bus protection in the bays, nor would breaker and a third; but you'd have to have dedicated bus protection in each bay where you have two breakers with nothing between them.
To the original question, I think I'd trip both of them simultaneously but hope that I never have to turn that from a theoretical answer to a practical answer.
To date I've not had to deal with critical clearing times that would cause one to entertain such outlandish schemes;
but I've heard of conditions that would make something of the sort a reasonable reaction. I think, though, if I ever got there I'd try to have the extra breaker on the position. The bay, from bus to bus, would still have only three breakers for two positions, but then I'd add a single breaker (possibly with a bypass switch) on the line or transformer.
Then I'd have a 4 or 5 cycle breaker failure trip of that breaker followed by the 10 cycle (our standard, others might be 7 or 8 cycles) breaker failure trip of the adjacent bus and the far end of the bay. I'd like to keep that as a pencil and paper exercise.
Marks1080 said:Mbrooke: Security is reduced because you've added 'stuff.' One of the balancing acts between reliability and security.
So I agree with you when you say the double bus double breaker is more reliable. But my point is that the very small amount of reliability you gain doesn't justify the cost and decreased security. Security is decreased just by adding more elements which could represent a failure point. Generally, "A station with more breakers than another station will experience more breaker fails." is a true statement.
You want to consider real life scenarios where you gain anything by having a double bus double breaker. It's easy to imagine those scenarios. Now try to find real life situations where they happened and how double bus double breaker would have helped.
If you can actually find these scenarios ask how adding the extra breaker would have helped. After finding that out ask yourself if it would have been worth the cost to get that extra reliability. I think you'll find the answer to that is 'No' because there simply haven't been enough of those operations to justify catering for above a breaker and a half configuration.
Add with the security you lose by adding the extra breakers, the answer should most definitely be "No". This is why you see breaker and a half used so much. Like I said originally, unless you have a very special customer connected, where a loss of power equals a large law suit, or it's some large generating station critical to maintaining system stability, generally the best solution is breaker and a half.
This discussion actually reminds me of a book I read called "Confessions of an Economic Hitman." At least I think that's what it's called. It's about an ex-CIA operative who worked with American utilities who went over seas to build power systems for third world countries. One of his CIA duties was to get these countries to over build their power systems to a point where it was just indebting them to American companies for no good reason. This guy would have built plenty of double bus double breaker stations I'm sure.