tin2779
Electrical
- May 26, 2007
- 38
I have a 225 A molded case thermal magnetic breaker. I beleive it is 80% rated that means it is 185 A continous rating. I have three fans 75HP, 75 HP and 65 HP at 600 V. The total ampacity FLA is 210 A. That means I am overloading this breaker. I am not sure, how this will effect the thermal trip unit.
My concern is when two 75 HP are already running and 65 HP fan comes in to picture. Six times 65 A+ 150 A= 450 A for the total inrush cycle which will be around 2 secs for a typical NEMA design B motor.
My question is, Is there a possibility that brining this third fan coming online might drop the voltage to 80% and might open the contactors of already working fans and if eventually if the continous current remains 210 A, it might trip the therma unit of the breaker.
Any suggestions, if this will work.
Thanks