SteelPE
Structural
- Mar 9, 2006
- 2,759
We were recently contracted to design a foundation for a metal building. It seemed simple enough at the time until our client informed us that we had to certify that the building was in compliance with ASCE 24 “Flood Resistant Design and Construction”. I have never had to deal with these requirements before and I find them a little confusing.
The building is located in a V16 zone with a BFE (Base Flood Elevation) = 17’. The elevation of the SOG is at 7.5’ meaning our structure will be 9’-6” below water when the design flood occurs. This particular structure will house a facility that manufacturers/repairs boats. The second floor of this facility is located well above the flood elevation (23’ off the slab on grade). Basic Wind speed = 110mph.
I am a little confused with the requirements for breakaway walls. I know I need them because the building is located in a V zone. However, wall needs to fail at a maximum of 20psf unless certified by an engineer or architect under the following conditions:
1) Breakaway wall collapse shall result from a water load less than that which would occur during the base flood.
2) The elevated portion of the building and supporting foundation system shall not be subjected to collapse, displacement, or other structural damage due to the effects of wind and water loads acting simultaneously on all building components (structural and non structural).
Because the wind loads are greater than 20 psf I have to certify the wall will fail under the above conditions. Can I design the stud wall to fail under 1.5x the wind load (which will be less than the hydrostatic load) and have the Metal Building Manufacturer make the required adjustments to the design? How do I go about certifying that something is going to fail when most codes deal with safety factors? Am I worried to much about this?
The building is located in a V16 zone with a BFE (Base Flood Elevation) = 17’. The elevation of the SOG is at 7.5’ meaning our structure will be 9’-6” below water when the design flood occurs. This particular structure will house a facility that manufacturers/repairs boats. The second floor of this facility is located well above the flood elevation (23’ off the slab on grade). Basic Wind speed = 110mph.
I am a little confused with the requirements for breakaway walls. I know I need them because the building is located in a V zone. However, wall needs to fail at a maximum of 20psf unless certified by an engineer or architect under the following conditions:
1) Breakaway wall collapse shall result from a water load less than that which would occur during the base flood.
2) The elevated portion of the building and supporting foundation system shall not be subjected to collapse, displacement, or other structural damage due to the effects of wind and water loads acting simultaneously on all building components (structural and non structural).
Because the wind loads are greater than 20 psf I have to certify the wall will fail under the above conditions. Can I design the stud wall to fail under 1.5x the wind load (which will be less than the hydrostatic load) and have the Metal Building Manufacturer make the required adjustments to the design? How do I go about certifying that something is going to fail when most codes deal with safety factors? Am I worried to much about this?