Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

boosting from 120 to 277

Status
Not open for further replies.

scruf

Electrical
Joined
Dec 20, 2004
Messages
1
Location
US
Is there any such thing as a single phase transformer that you can get 277V (for a lighting circuit) from 120/208 source. Can you get this done with a coulple of buck/boost transformers or is this totally the wrong approach?

The reason for the inquiry is perhaps to save some $ to change out a bunch of expensive 277V 1% dimming ballasts. This is a health care application where I have to put some selcted fluorescent fixtures on a critical branch source that has no 277 within several floors of the main electric room. The load in this case would be real small, around 600VA-1000VA
 
yea: you can boost to 277 from 208 , check with the mfg representative of the buck boost selected. They will help you select the kva and furnish you with a diagram.try seimens, ge, acme, etc. if you are the guy doing the hareware connection then they are a little tricky so be careful not to mix circuits up with other loads. basically it's just an autotransformer and works like a step up coil.
I don't like using them because someone else may try to use the circuit for something else and cause trouble. your best bet is to use a standard step up transformer with a panel board. Because you will find that other loads will crop up in the future that need more 277 volts lighting. buck boost are kind of a work around method for one shot application. most people don't use them because they are odd ball and have cause troubles with mis-applications.
 
I just remembered-code will not allow you to go from 120v to 277V with a buck boost ( it is too great a step up) and I think that the lights from UL are rated 277 (from neutral to 277v) so I don't thnk it is allow. Use a step up transformer with panel board. good luck
 
 
One kVA is about 8½ amperes at 120V and under 4 amps at 277V, and by NEC 450 a transformer with 2-wire primary — 2-wire secondary could be protected by a primary overcurrent device alone.

Typical is "Group VI".
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top