Booster pump for cooling coil
BearsFan2
3
Hello All, I have an application where I need to install a new cooling coil in an existing 30% water/ glycol distribution loop. The existing distribution loop has a 50 psig differential pressure set point across the supply and return piping maintained by a VFD driven pump. At full flow the new coil needs 90 psig. The existing pumps are not sized to provide any added pressure. I want to install a booster pump to the supply pipe to the coil to provide this added pressure.
Who makes this type of pump? Any pitfalls with this approach? All help is appreciated.
Good spot for Primary-Secondary pump. Secondary pump will handle the new coil, and not upset the main loop. Pumps by Bell & Gossett, Taco, Armstrong, Goulds will work.
I have never heard of a coil requiring 90 psig. Must have lots and lots of rows.
We seen coil loop pumps often. What you're proposing is normal. The trashcanman gave you good pump manufacturers.
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
must be a huge system a 50 psi and 90 psi coil drop.
I (and all my maintenance staff) would recomment to never isntall Taco / Armstrong. Unless leaking is not a problem. Especially since glycol leaks even more than water.
Um, forgive me for being a moron… 50 psid DP (pounds per square inch, differential) in your existing loop is extremely high. What device needs that DP? 90 psid for your new coil is 208’ head, where a normal coil might be 10’-15’ head. Are you talking about a process outside of HVAC?
Hello All, yes this is a special coil, 2 stage coil, 68 gpm at 90 psig data is straight from the manufacturer. This is 100% OA unit cooling aircraft(jumbos) parked at the gate.
Ok. I'd suggest Grundfos. And yes, series pump installation is appropriate to boost pressure at this coil.