I would like to design a bollard (and its sonotube footing)to behave as a guardrail in a parking lot... essentially, for a horizontal force of 5kips @ 2 ft above ground. I'm using a 6"OD pipe embedded into a 24" sonotube (4.5 ft deep in the ground).
Is there a code for bollards, or using geotechnical engineering principles will suffice?
Mover = 5x2 = 10kip-ft
Mstab = 8.58 kip-ft
Maybe there should be an allowance for deflection rather than keeping the bollard rigid?
Is there a code for bollards, or using geotechnical engineering principles will suffice?
Mover = 5x2 = 10kip-ft
Mstab = 8.58 kip-ft
Maybe there should be an allowance for deflection rather than keeping the bollard rigid?