DB&B is a class of isolation called "positive energy isolation" Positive energy isolation is required to protect workers during certain evolutions. That is the only time that I know of that it is required by law. There are many ways to accomplish positive energy isolation including: (1) insert blinds; (2) removing or misaligning piping; or (3) double block and bleed. The first two are appropriate for any work evolution. The third has some restrictions where it can be used.
Now, a designer can choose to provide built-in positive energy isolation for the kinds of things that BigInch mentioned. That is prudent design, not usually mandated.
So for the OP question, install permanent DB&B or not depending on your expected risk profile. It has nearly nothing to do with the design pressure in your line.