ZShan
Structural
- Oct 4, 2010
- 1
Our team hasnt designed piles before but we came accross a request from Geo Tech to design a pile of 1.5m diameter with 28 bars of 40mm dia.
Quite a massive pile to resist a bending moment of 5000 kN.m
As I said, I am not an experienced engineer and never had a chance to design piles but the Geo Techs were interested in the design which ignored the axial load effects to make the bending moment worst. So I approached the design with generic solution.
One of my colleague designed the section on SAM Leap program and found out the bending capacity to be 7800 kN.m
I found the capacity to be 9000 kN.m by my section analysis. For the past 4 days I have been trying to figure out if I have done it wrong but cannt find anywhere anything wrong about my approach.
here is what I have done:
-Assumed the max strain in concrete to be no more than 0.003
-BS 5400-4 fig 1 and 2: 3 modes of reinforcement strain. Elastic, partial plastic and full plastic.
-Drawn the strain diagram with assumed depth of Neutral Axis (adjusted NA later on to equalize compressive force against tensile force).
-Calculated the strain in each reinforcement bar at different levels
-Ajdusted the values of strain found in the bars to max plastic strain, so that no bar is having more than max plastic strain.
-Calculated the stresses (compressive and tensile) based on this adjusted stress.
-Calculated the forces in each bar based on this stress.
-Calculated the moment, each force in the bar will induce at the Neutral axis.
-Calculated the area of concrete above the neutral axis and adjusted it for the reduced stress block.
-Calculated the moment of this area with Neutral Axis.
-Added both these moments (from reinforcement and concrete) which came out to be 9000 kN.m
Can anyone tell me whats wrong with my approach to the solution? (considering all calculating errors are elimnited).
Thanks.
Quite a massive pile to resist a bending moment of 5000 kN.m
As I said, I am not an experienced engineer and never had a chance to design piles but the Geo Techs were interested in the design which ignored the axial load effects to make the bending moment worst. So I approached the design with generic solution.
One of my colleague designed the section on SAM Leap program and found out the bending capacity to be 7800 kN.m
I found the capacity to be 9000 kN.m by my section analysis. For the past 4 days I have been trying to figure out if I have done it wrong but cannt find anywhere anything wrong about my approach.
here is what I have done:
-Assumed the max strain in concrete to be no more than 0.003
-BS 5400-4 fig 1 and 2: 3 modes of reinforcement strain. Elastic, partial plastic and full plastic.
-Drawn the strain diagram with assumed depth of Neutral Axis (adjusted NA later on to equalize compressive force against tensile force).
-Calculated the strain in each reinforcement bar at different levels
-Ajdusted the values of strain found in the bars to max plastic strain, so that no bar is having more than max plastic strain.
-Calculated the stresses (compressive and tensile) based on this adjusted stress.
-Calculated the forces in each bar based on this stress.
-Calculated the moment, each force in the bar will induce at the Neutral axis.
-Calculated the area of concrete above the neutral axis and adjusted it for the reduced stress block.
-Calculated the moment of this area with Neutral Axis.
-Added both these moments (from reinforcement and concrete) which came out to be 9000 kN.m
Can anyone tell me whats wrong with my approach to the solution? (considering all calculating errors are elimnited).
Thanks.