THD is usually thought of as what the power supply will reflect BACK to the source. Are you saying that your test fixture must have a source with less than 2% THD on the incoming terminals? That's fairly strict. The best I have ever seen is Sola ferroresonant power conditioners with output THD at 3%. Most others, even "medical grade" conditioners are 5%, if they have a rating at all. You may need to contact someone like them to see if they can customize one for you. You could theoretically make your own harmonic trap filter on the output to see if you can improve on that, but it would be tricky given the nature of ferroresonant transformers. I would not attempt it, but then, it isn't my field.