That's a good question.
The original device was used to predict life of bearings, based on measured discharge (EDM) activities in the bearing during commissioning. If activities were low, then nothing more needed to be don. If high, a common-mode filter, a du/dt filter, equipotential connection or a shaft grounding device needed to be added. We then checked to see that EDM was acceptable, which it often is when you have done the right thing.
There are a few rough limits that have been verified throughout the years: If there are more than 10 PPS (pulses per second) from 20 V, or more than 100 PPS from 10 V, then bearing life will usually be less than one year. If there are hundreds of PPS at 20 V, then life may be as short as one or two months.
Also, if peak voltages are above 5 V (peak voltages are measured as representative levels that occur at least 1000 times per second), then life is also potentially at risk, even if no EDM is detected. The reason is that the speed may be high or oil film cold and then, there will not be as many discharges as when speed decreases or temperature goes up.
When we sought for a good name, I first thought of Karin (she is good at finding certain types of faults). But at last we changed it to Bearing Predictor 1 or B.P.1 for short. And if you pronounce B.P. it sounds like Beppe. Beppe was a popular actor in Sweden and the name caught on.
Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.