IDS said:
Not saying you are wrong, but what is the justification?
Right after the word "justification" in my previous post, I listed the three justifications that I'm most familiar with. And that's the lion's share of what I've got in my bag of tricks. Note that those things reflect less my own personal opinions than they do the opinions of others practicing in my market.
When I choose a low axial utilization ratio over a detailed look at eccentricities, my own "justification" is really:
1) I simply do not perceive that the world has a meaningful gravity post problem. One has to pick their battles as a structural engineer and this isn't the one for me. I feel that structural designs, and structural drawings, often have more serious deficiencies and that more attention in those areas represents a better return on investment.
2) As a structural engineer, I view myself as a moderately skilled, rough proportioned of things. As an industry, I feel that we tend to get too obsessed about accuracy in a space where any rational person must acknowledge that little meaningful accuracy is available to be had.
Now for a fun anecdote.
One of my first assignments as a newly minted graduate engineer was the design of a bunch of steel columns in a one story joist & beam building. My boss was an interesting character in that he was a
very practical engineer but would never, ever utter the phrase "overthinking" to me. He'd adjust schedules and hemorrhage fees at will if that's what it took to buy me the space to do whatever I felt needed to be done. I think that he mostly just kept me around for company (two man dept) rather than production.
What I felt needed to be done was to check all of the "posts" for moments at the top and bottom arising from eccentricities in the two to four incoming framing members which may be pattern loaded. I had oodles of cases to check, oodles of things to consider, and built myself a giant spreadsheet to help. It took me the better part of two days and I almost choked on the assignment altogether. At the end of it, I asked my boss how he typically handled this stuff. I was ready to give up engineering and take up accountancy.
He said that, for a gravity post of a typical cross section and with typical shear connections, he ignored the eccentricity but kept the axial utilization under 80%. I looked at my numbers, realized that would have worked comfortably in all cases, and agreed that was a rational approach. 90 seconds per column design without the aid of software. More time to add missing details to the drawing set and wonder if the entire building might rack over sideways.