hokie......belated response to this;
jfmann,
Do you disagree with my statement of 1 Feb, 01:51?
"Interesting again, but the loadings are not the same. For a simple spanning lower beam and also a simple spanning upper beam over the half span, both with the same I, and loaded uniformly but ignoring self weight, the bending moments are the same, wl^2/8".
Do not understand what you were getting at .......however, for stated case (or for any position of upper beam (length L/2) along lower beam, of length L) bending moments are not the same. Span is of course different for each beam......and, for stated problem, there is no load on lower beam other than load distributed to it by upper beam.
For upper beam centered within span of lower beam, uniform load on upper beam only and stiff upper beam (contact only at ends of upper);
M-upper (max) = wL^2/32 M-lower (max) = wL^2/16
For completely flexible upper beam (with full contact).....which is same as having no upper beam......M-lower (max) = 3wL^2/32.......which equals sum of the 2 maximum moments for separate beams with contact only at 2 points.
For stiff upper beam........moment in lower beam is 67-percent of moment without any upper beam.
For configuration with one end of upper beam at midspan of lower beam;
For stiff upper beam (contact at ends only)........moment in each beam remains the same: M-upper (max) = wL^2/32 M-lower (max) = wL^2/16
For completely flexible (or no) upper beam;
M-lower (max) = 9wL^2/128
For stiff upper beam.........moment in lower beam is 89-percent of moment without any upper beam.
For any stiffness of upper beam (located entirely within span of lower beam), lower beam must still support entire load......such that maximum shear at support is not reduced, which is not entirely consistent with notion of load sharing (if defined as "taking load away" from some other element).
Consider upper beam as header beam several feet above lower beam, supported on 2 posts, with some load on this header beam only. Not including weight of posts, this setup results in the same loading condition as for upper beam on lower beam without posts. Yet it is somewhat of a stretch to consider configuration of header beam to be "load sharing" condition, even though, compared to same load supported directly on lower beam, bending moment and deflection of lower beam is reduced...........as thoroughly documented by discussion.....and SRE model (with fine documentary photos) above.
John F Mann, PE