Maypot, Sorry, I am returning to this thread late.
YogiBear1, Bagasse boilers are solid fuel stoker fed over sloped or dump grates normally, and in his case, without auxiliary fuel, more than likely without flame safety systems and probably only the most rudimentary of combustion controls (proportional only). What you are recommending is way beyond the scope of this boiler.
However your approach is right on, and I see you agree with my earlier post about the potential for the gasification of the fuel bed.
Maypot, the controls logic that Yogibear1 is recommending is a sequence in boilers where before the igniters can be engaged a sequence of operating the fans and dampers in order to pass a certain amount of fresh air through the boiler to purge out any remaining fuel is gone through.
Since your boiler probably lacks the control systems that control that it is not applicable to your situation.
Regarding your fuel situation on an emergency stoppage,you have two choices in this occasion. You can either burn out the bed by continuing to run the ID fan and burn the fuel and make what steam you can until the fuel on the grate all burns up, or you can manually remove the fuel.
This can be done by dumping it into the ash pit if you have dump grates, or by raking it out through the furnace doors onto the floor. I have done it both ways. I prefer raking it out, because in the ashpit it still can burn and cause problems in the furnace. I would note that I hate handling those hot rakes and dragging that stuff all the way to the door, and then having to work over the pile of burning fuel as I dragged the next rake load out the door.
The increase in pressure you asked about is most likely due to the moisture and/or volatile gas coming off the fuel pile which being wet and thick enough to put the fire out, most likely blocked the airflow through the grates as well. To make this statement, I am assuming that you would have stopped or closed the dampers on your ID fan upon encountering the stoppage.
The situation that YogiBear1 and I am referring to is the introduction of fuel into a hot furnace without adequate airflow to promote complete combustion and removal of the gasses, but with enough residual heat in the furnace due to radiant heat from the refractory as well as heat in the fuel bed below that it sat down on top of to provide sufficient heat to dry it and to drive the moisture and volatile gasses off of it. Without adequate airflow and purging to remove it, if the volatile gas builds up and finds a glowing ember, hot piece of ash, refractory or flame source of any kind, maybe something is still burning over in a corner of the furnace, it will ignite and if there is enough of it, explode.
YogiBear1 and I suspect that this is what puffed your boiler.
If you ever look into the furnace when you have a good fire and see a real blue flame near an air jet or air port, you are seeing the volatile gasses burning at that point.
Bagasse, as well as bark, sawdust, etc, solid fuels that are around 50% moisture go through the following steps. The fuel enters the furnace basically at room temperature or slightly above, (depending to some degree on the temperature of your imbibition water). In order for the bagasse to ignite, first it has to heat to 212F in order to boil off all the water in the fuel and dry out. From that point, then it has to heat up to the igniton point I(I don't remember what that is for bagasse) where it then catches fire, and begins to burn.
As it gets lighter as it looses moisture and volitales, it will try to lift off the grate if there is sufficient air flow. If it lifts, and is entrained in the upward furnace gas flow and enters the boiler tube banks, there the temperature is not sufficient to maintain combustion, and the flame will be quenched resulting in LOI or CO.
I don't think I got an answer to a question in another thread as to whether this boiler had FD fans, and/or air preheaters. Air preheaters help the combustion process of moist fuels immensily, since they heat the air to the range of 4-500F which helps drive off the moisture in the fuel much more rapidly so combustion can begin.
Therefore, I recommend for any stoppage that is going to amount to more just a very few minutes, (fixing a broken conveyor is not going to be rapid) that you keep your ID fan in service until you burn the bed out, and then start over when you get fuel flow back. With a hot furnace it won't be as difficult starting a cold boiler. It will restart quite rapidly.
Ask if you don't understand any of this.
rmw
PS, what is your mill's TPD grinding rate?