BASE SLAB WATER TANK

Status
Not open for further replies.

bazflexure

Structural
Feb 5, 2009
37
I have query regarding design of base slab in concrete underground water tanks.
Will the moments from wall be transfered to base slab?

Thanks in advance.
 
Replies continue below

Recommended for you

The wall will deflect and develop moments according to how you reinforce it. So, if you design and reinforce the connection of the wall to the slab as a pin connection, then the empirical answer is no. In actuality, there is probably small amount of moment, but I would ignore it.

Mike McCann
MMC Engineering
 
can you really get a water tight connection suitable for a tank with just a pinned joint?
 
Possible, but not recommended - build keyway with water stops, add compressible/expandable joint sealers..
 