Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Steven, I like and respect you. But, respectfully I have to throw the flag on this one.For a graphical approach, draw your delta wye, show 1pu current leaving each wye leg in phase to represent the zero sequence currents. On the delta side you will have 1pu in each winding, all in the same direction. Summing the currents to zero at each delta node shows that no contribution from the primary lines are needed. If the nodes are remote from any of the windings, there is little difference.
You're being too harsh on Steven. He was discussing only the zero-sequence currents. The primary lines do not contribute zero-sequence currents. As I noted in my previous post, you can have zero-sequence currents in a winding while the total current in the winding is zero. Similarly, you can have current in the line without zero-sequence current in the line.Steven, I like and respect you. But, respectfully I have to throw the flag on this one.A transformer bank with full load on the secondaries and no contribution from the primary lines?? Is this patentable?I was starting to doubt myself, but now, considering the high caliber of the other parties to this discussion, I suspect a massive misunderstanding of some sort.