ElectricPete,
People have been burning up motors for years because they have mistakenly
multiplied the motor FLA by the SF number and operated them in an overloaded state. While it is rare to see such a failure in the first thirty days of operation...failure does occur over time as the motor life is consequentially foreshortened.
The amps do not track the power because of the power factor; which
increases when the motor is loaded above rated. As a consequence, the
increased power (rated power x PF)....occurs at an amperage value that is
less than FLA x PF number). So, as any motor manufacturer will tell you,
operating at the SF x FLA will result in an overloaded motor.... and one
which will void the warranty.
I would be remiss if I did not also address the issue of efficiency as the motor is operated into the service factor. Efficiency does drop off some as the load is increased above 100%. So, the the increase in current due to loss of efficiency is somewhat offset by the increase in power factor. I leave it to others to decide the resultant consequence. But from tests made on a dynamometer at a major motor manufacturer, I can say that you get to the SF power at a value less than the SF x the rated amps.
Now then, to get back to tmo42's original post, operating the motor at the SF
on inverter power can cause the motor to overheat and/or operate
overloaded as it negates any margin for harmonic heating in the motor. Many
motor manufacturers who rate their motors for definitive use on inverter
power, will rate them as follows:
1.0 SF Class B rise on sinewave power
1.15 SF Class F rise on Sinewave power
1.0 SF Class F rise on inverter power
Such motors typically have class 'F' insulation.
For tvo42 I would suggest he have a conversation with Baldor to see
what FLA they sanction for the particular motors when operated on inverter
power. You may find that you cannot use the Service Factor while operating on inverter power or you may not be able to use the full measure.
And lets not lose sight of the fact that not all inverters are created equal.
Differences in modulation schema do have considerable impact upon the
harmonic content in the consequent output waveform. Tests run on various
manufactures that employ sine-coded or star modulation show that the rms
fundamental output voltage can be down by as much as 82% from the rms
fundamental of the applied mains voltage. Consequence is that the motor
operates voltage starved, having to slip more to produce a given value of
output torque. Thus, less torque per ampere means that more amperes are
required to produce the same value of torque.
Oh, and using an ammeter to observe the motor amps when on inverter power, can lead you astray too. The ammeter, even the true RMS types, will show you the total current; that is, the fundamental + the harmonic currents.
Only the fundamental produces useful torque.... some of the harmonic currents/torques actually subtract from the delivered shaft torque.
Interesting, isn't it, that what you see, is not necessarily what you get.
So the decision to operate into the service factor of a given motor should not be made lightly. There are many factors to consider before taking the leap.