Hi Tmo42
I have just finish load tetsing 4 - Baldor motors and the 4 VFDs that will eventually drive it.The unit has a Single front end and 4 inverters.One of the Inverters is water cooled ,the other 3 are air blower cooled.
We ordered these motors from Baldor for a specially project.1- 200 hp for a VIB Screen,1-600 for an Impactor /crusher and 2 -600 hp for Slurry Pumps.
The windings are Inverter duty of course,with Class F
insulation with Class B Temp rise.
I am somewhat confused by the talk of SFAs and what it suppose to mean.
The motor nameplate shows the motor FLAs.It does not care if the S. factor is 1/1.15/1.25 or whathave you.
Overloads are set normally at a max of 1.25 of motor full load current(FLC).Service Factors are related to H.P not to nameplate FLAmps.
I don't know how large your motors are,but regardless of the size,electric motors should not be operated at their service factors on a continuous bases.The Factor is in place to allow for momentary process changes,voltage variations,or amb.temp changes.If you operate your motors at SFactor you lost the ability to deal with these variations and run the chance of severelly overheating your motor.For every 10 Dec inc. above TRise your motor life is reduced by a half.(I guess you all know that)
TMO42-I don't know where you are located,but I do know the name and PH # of a Baldor Rep in our area that was most helpful with all the info we needed during the tests.If it Ok with him I'll give you the Ph #.
I asked this fellow to get me the Data sheets for the windings,showing Stator slots /Rotor slots and I had it in my hands the following day.I don't recall many of our Suppliers being that forthcoming.
Hope it does not confuse the issue even more.
GusD