B-H Curves of Large Power Transformers

Status
Not open for further replies.

Bronzeado

Electrical
Joined
Jan 6, 2008
Messages
272
Location
BR
Hi folks,

In general, transformer manufactures can not measure the complete B-H curve (based on the V-I curve) of large power transformers (above 100MVA). This is because of the small short-circuit power in their laboratories which is not enought to saturate deeply large transformers.

Normally, they measure the V-I (B-H) curve of the winding on the ferromagnetic core supplying voltage up to 120% of the nominal voltage. Then, they measure the V-I (B-H) curve of the winding without the transfomer core (air core reactance) and, graphically, join these two curves.

My question is:

1) At which point these two curves should be joined?

2) Is that point the "knee point" of the B-H curve?

Best regards,

Herivelto Bronzeado
 