automatic air vents

Status
Not open for further replies.

ELMROAD

Civil/Environmental
Aug 1, 2008
1
Hot water systems (commercial buildings)Question: Is it still valid to use automatic air vents at the top of service loops?
 
Replies continue below

Recommended for you

Manual vents are better in concealed locations.

Keep the auto vents at the air separator where, when they fail, and they will, they don't make a mess.
 