Hi MJC,
Thanks for reply.
Our boiler Design at 250 psig.
Htg. surface is 538 sq. ft and stem. cap. is 4317 lbs/hr.
We shipped this boiler with only one 2" relief valve cplg, but as per ASME sec i, pg-67.2, min. 2 valves req. for this cap. of boilers.
Now either we'll have to add one more cplg. or will have to use "Y" fittings and mount two valves on one cplg.
From where i'll find "y" fitiing or can we use any forged fittings for that?
so pls. advise me what best i can do for this case?
pls...ASAP
thanks
Mihir