While performing some calculations on an exterior masonry wall I have seem to find a discrepancy in the masonry code.
Previous versions of IBC allowed a load reduction for two or more variable loads in a load combination. IBC has removed this portion of the code in favor of including the provision directly into the load combinations in IBC 2006. In the analysis of a member only affected by wind load and its own self weight this reduction is not allowed.
I was having trouble getting an exterior wall to work using the Allowable Stress Design method when someone from this forum suggested looking at the wall using Strength Design. I was shocked to find that there was an increase in the capacity of the wall by nearly 50%. I attribute this to the IBC not allowing the 1/3 stress increase that is located in 2.1.2.3 of ACI 530-02 (my ACI530-05 is in the mail).
Here are some quick numbers:
For ASD #5 @ 24 provide Ma = 11,831 in-kips.
For Strength Design #5 @ 24 provide phi-Mn = 28,329 in-kips.
Divide this by 1.6 to go from strength design to allowable design in the load combinations (for comparison only) and you get 17,706 in-kips. 11706/11831 = 1.497
I was wondering if anyone has run across this discrepancy before?
Previous versions of IBC allowed a load reduction for two or more variable loads in a load combination. IBC has removed this portion of the code in favor of including the provision directly into the load combinations in IBC 2006. In the analysis of a member only affected by wind load and its own self weight this reduction is not allowed.
I was having trouble getting an exterior wall to work using the Allowable Stress Design method when someone from this forum suggested looking at the wall using Strength Design. I was shocked to find that there was an increase in the capacity of the wall by nearly 50%. I attribute this to the IBC not allowing the 1/3 stress increase that is located in 2.1.2.3 of ACI 530-02 (my ACI530-05 is in the mail).
Here are some quick numbers:
For ASD #5 @ 24 provide Ma = 11,831 in-kips.
For Strength Design #5 @ 24 provide phi-Mn = 28,329 in-kips.
Divide this by 1.6 to go from strength design to allowable design in the load combinations (for comparison only) and you get 17,706 in-kips. 11706/11831 = 1.497
I was wondering if anyone has run across this discrepancy before?