Noticed the cosmetic ones. Does not say a lot for the editors and stylists.
Re 8.1.10.6(c), Agreed it does not comply, but I think the justification would be that 25% could have been terminated much earlier, but no sensible engineer would terminate multiple times so the 1st 25% termination point has been extended to be at the same location as the second where a total of 50% has been terminated. This clause is a deemed to comply requirement for the for reinforcement termination based on the real clause 10.4 which also has the 25% termination rule, but it is based on terminating at the point where the reinforcement is no longer required by calculation of strength and development requirements rather than a deemed to comply requirement.
I also do not like end support being shown as a masonry wall and no development of top reinforcement as the deemed to comply case. Most beams would terminate at a column and require proper top reinforcement detailing.
Cannot comment on reasons for the release delay. Most people in the industry know what went on!