Elie2
Electrical
- Aug 14, 2004
- 8
Hi,
I have a 100kVA load 300m far from the substation and i had to run 3 cores for the 3 phases and 1/2 core for the neutral and 1/2 core for earth.
I did install an earth pit near the load but i put the 1/2core cable as well so that the earth will not be the only return path for the fault.
Now that everybody is happy and the money was paid, please someone correct me - isn't this a complere waste of money and duct space for the earthing cable? I mean as per 250.4 (B)4:
Electrical equipment ... shall be installed in a manner that creates a permanent ... to the electrical supply source to facilitate the operation of overcurrent devices should a second fault occur on the wiring system.
Ok. My 2 questions are:
1. If at the MDB i do NOT have RCDs or any other earth fault sensing equipment, then i do not need this cable - right?
2. What type of second fault can happen that will help trigger the breaker?
In my opinion: the resistance of the earthing cable over 300m is still much less than the 5 Ohms of the earth pit, so that the code does not want the short circuit current limited by the increased resistance - but still is is the magnetic unit around the faulty Phase in the circuit breaker that will interrupt this LE fault.
The purpose of the earth pit near the load reduces the touch voltage in case someone touches the metallic body when it is faulty.
Any clarifications is appreciated and thanks
I have a 100kVA load 300m far from the substation and i had to run 3 cores for the 3 phases and 1/2 core for the neutral and 1/2 core for earth.
I did install an earth pit near the load but i put the 1/2core cable as well so that the earth will not be the only return path for the fault.
Now that everybody is happy and the money was paid, please someone correct me - isn't this a complere waste of money and duct space for the earthing cable? I mean as per 250.4 (B)4:
Electrical equipment ... shall be installed in a manner that creates a permanent ... to the electrical supply source to facilitate the operation of overcurrent devices should a second fault occur on the wiring system.
Ok. My 2 questions are:
1. If at the MDB i do NOT have RCDs or any other earth fault sensing equipment, then i do not need this cable - right?
2. What type of second fault can happen that will help trigger the breaker?
In my opinion: the resistance of the earthing cable over 300m is still much less than the 5 Ohms of the earth pit, so that the code does not want the short circuit current limited by the increased resistance - but still is is the magnetic unit around the faulty Phase in the circuit breaker that will interrupt this LE fault.
The purpose of the earth pit near the load reduces the touch voltage in case someone touches the metallic body when it is faulty.
Any clarifications is appreciated and thanks