Here is some more info.
The machines are class F (and are not derated for class B temp rise) with closed cooling (TEFV). 3 wire RTD’s are correctly calibrated to cancel lead resistances. The VFD is a 4 section IGBT directly feeding two terminal boxes on the motor, where the motor is delta connected. The winding is 8 circuit delta. All the 12 RTD’s show temps higher than 140 deg C. When I ran the motors in open shaft at 750 RPM/50Hz thru’ the VFD, the winding temps stabilized at 75 deg C after two hours with a cold air temp of 28 deg C and the motor body temp at 33 deg C. The stator winding copper is liberally (or conservatively??) designed with 2.2 Amps per sq mm. As suggested by GordS, I had already taken the winding temp readings when VFD was shut down and found no step drop in the temp readings at DCS.
Now for the basis for my doubts about RTD’s getting affected (i.e. heated) by VFD:
1. As I mentioned in my posting, the motor body temp at the load of 1200 Amps at 600 RPM (when the RTD’s were showing over 140 deg C) was only 50 deg C. I would expect a much higher body temp with such high winding temps.
2. Both the stator winding condition during inspection (at over 140 deg C operation, in my experience of two decades, I expect to see some discoloration of the winding) and the very low current density (especially at 1200 Amps, it is only 1.5 amps per sq mm, which is normally used in copper bus bars where we don’t see such high temps notwithstanding an enclosed structure like a motor body) argue against such high winding temps indicated.
3. In open shaft condition, the winding temps are high at 75 deg C when the stator current was only about 400 Amps and the motor was running at the rated 750 RPM (thus ensuring adequate cold air flow).
4. Also, the rotors do not show any indication of overheat (the bare copper bars or the core do not show any discoloration).
vanstoja : you mentioned “motor's power factor will be degraded causing higher than speed-cubed-proportional running current. This is reflected in the 1200 amp current that is 33% higher than the 901 amps that would result from the 80% rated speed operation assuming no power factor”. Could you please expand on that ?
GordS : Yours was a good suggestion which I had already carried out. But, if the RTD’s were getting heated by the VFD, being located in an area where there is no cooling medium, will not the RTD’s temp drop slowly (as against a sudden drop) ?