High Bronzeado,
The DC filters not only are designed to reduce telephone interference but also noise induced in power line carrier (PLC),radio, maritime,military applications,railroad signal, and others communications in a wide frequency bandwidth.
In many countries, the interference of power lines with communication systems is regulated by government agency or independent organizations. For example, In the USA the interference issues are within the jurisdiction of the Federal Communication Commission (FCC). Check in Brazil if the Minister of communication ( Agência Nacional de Telecomunicações/ ANATEL or similar) could help in this matter.
If the converter stations are VSC (voltage Source Converter) or/and interconnected with cables (usually with high capacitance), there is high hope that DC filter may not be required. However, judging for the length of the line (2500 km) most likely this project may be designed in bipolar configuration using LCC (Classic) technology with overhead DC lines. Therefore, this may require more considerations and engineering judgment to justify the DC filters.
In addition with the government regulations and local compliance issues, the following suggestions might help with the DC filter options:
• Check the level of superimposed harmonics in the DC side. (See sample of enclosed graph)
• Analyze the impact on extra losses cause by multiple of the characteristic harmonic (n.12). verify if the cost of installed DC filter is higher than the savings
• Validate the system performance of DC filters with smooth reactor regarding limiting the rapid rise of current flowing into the converter in the event of valve misfiring during commutation.
• Verify DC overvoltage levels particularly in the ground during monopole operating mode.
NOTE: Regarding the harmonics superimposed in the DC side, we should keep in mind that the DC rectified process is dealing with non ideal devices. For instance, transformer turn ratios and transformer reactance are not identical for the Y-Y & Y-D large converter transformers and the associated leakage are unbalanced in the AC three phases. As a result, unequal commutation reactance also cause non characteristic voltages on the DC side.