In the studies we do, we most often come across high incident energy on the main breaker on the 480V bus. Obviously, the main protects the bus, but not itself, thus the bus will typically have much lower incident energy. (Amazingly, some clients insist that the main protects itself while it is being racked in/out. . .)
We use many different approaches to remediate the incident energy depending upon the clients' particular situation and/or budget. I feel that fuses are a bad idea in most situations because it then makes protective device coordination difficult at best.
If you have solid state relays, it is possible to have a 'maintenance' setting with a TCC set for faster trip time. It would be activated by a maintenance switch. This may not be advisable if you are having large motors automatically starting while the relay is in maintenance mode - or if you have forgetful electricians. Another option to explore is a differential relay that includes the downstream main in the zone of protection, since differentials have a faster trip time. Also, you could just replace your equipment. I have one client whose equipment is 30+ years old and was planning to have a major upgrade soon, so it did not make sense to spend money on equipment that was to be replaced. Instead, he has decided to just accelerate his replacement schedule – and that project now has the blessings of his plant management too! So, it can really depend on your situation which path will work best.
These were just a few ideas, I hope they are helpful.
Best regards,
-Shane