Kiljoy
Electrical
- Apr 15, 2003
- 132
OK, this is a strange one. We build industrial machinery which we test in our shop via temporary pigtails to a fused bus system. Our QC guy was reaching onto a 480V panel to read voltage across the distribution block. All of a sudden, there was an arc flash. The distribution block he was reaching for didn’t have a mark, but the fuse block for the hydraulic tank heater about a foot to the left had it’s fuses melted on the tops only. They did not clear. His multi-meter probes were also melted. The main 400A molded case breaker disconnect did not trip, nor did the buss-plug fuses. I took apart the meter and power obviously went through it. Our guy swears he has the meter on voltage, was no where near the melted block, and was reaching behind some temporary wires to read voltage. The temporary run is SO cord from a VFD to a motor we use for testing VFDs.
Here’s the only thing I can think of. Either our very qualified QC guy is lying, or there was some sort of harmonic arc between the VFD leads and his meter. He swears that he was no where near the melted fuse block and that he hadn’t even touched the probes to the distribution block yet. He was wearing a nice metal watch and a ring (yes, not the smartest thing), but other than a slight UV burn from the arc, not a scratch on him.
Here’s the only thing I can think of. Either our very qualified QC guy is lying, or there was some sort of harmonic arc between the VFD leads and his meter. He swears that he was no where near the melted fuse block and that he hadn’t even touched the probes to the distribution block yet. He was wearing a nice metal watch and a ring (yes, not the smartest thing), but other than a slight UV burn from the arc, not a scratch on him.