I have a question about arc flash calculations. We calculate incident energy at the maximum and minimum values of fault currents provided by the utility. But in our case the utility only has the maximum value of fault current (minimum value of fault current is not available). So I will have to run the arc flash calculations for a range of utility fault current.
What should be the range of values for which the system be modeled to get the worst case incident energy? Should we assume the minimum fault current to be 5 times less than the maximum fault current; for example, if the given maximum utility fault current is 5kA, then should we assume the minimum utility fault current to be 1kA? Thanks.