A client has a 22kV swbd fed by 2 x 50MVA, 11% trfrs in parallel. The swbd has an internal arc flash rating of 25kA for 1s. The actual three phase fault level is 19.2kA and each trfr will trip in 1.56s.
I am concerned that the tripping time is too long and that the arc flash integrity will be violated for an actual 19.2kA fault. How do I quantify this?
I have considered using I1^2*t1 = I2^2*t2 with I1 = 25kA, t1 = 1s, etc. and get t2 = 1.3s. Clearly not good enough! But is this the correct formula to use for AF faults? If not how does one calculate t2? I have always advocated that if the plant rating is x seconds then the protection must clear the fault in x/2 seconds.
I have been advising the client to spend some money on buszone protection but it is an uphill battle. The dollars speak louder than anything else unfortunately.
Thanks.
I am concerned that the tripping time is too long and that the arc flash integrity will be violated for an actual 19.2kA fault. How do I quantify this?
I have considered using I1^2*t1 = I2^2*t2 with I1 = 25kA, t1 = 1s, etc. and get t2 = 1.3s. Clearly not good enough! But is this the correct formula to use for AF faults? If not how does one calculate t2? I have always advocated that if the plant rating is x seconds then the protection must clear the fault in x/2 seconds.