Applicability of ANSI C37.010

Status
Not open for further replies.

kartracer087

Electrical
Joined
Apr 18, 2020
Messages
72
Location
US
Does ANSI C37.010 emergency ratings definitions also apply to medium voltage (5-35kV) drawout circuit breakers? For example, say you have a substation with 84MVA transformers and you have an emergency 4-hour rating of 100MVA on a bus section. At 24.9kV, you would be over a 2000A breaker rating, so for that condition, could you in effect apply the provisions of C37.010 for that special case of a temporary overload?

Thanks,
 
Nevermind, I found that the C37.010 standard for emergency ratings does not apply to metal-clad breakers. So I guess it would be more of a question for the manufacturer. I think in my application above realistically you would need to apply a 3000A breaker in metalclad gear. Interestingly enough, most metal clad manufacturers do not offer 3000A breakers in 27kV construction, typically you would need to go with a 38kV unit. They are much larger and the structures are also much larger.
 