jcaiken
Chemical
- Sep 10, 2002
- 31
API 14C SAC A.4.c.5 seems to indicate that a PSV is required on a pressure vessel (max pressure >5 psig) unless it is the final vessel on a flare header (i.e. Flare KO Drum). However, this implies that any other vessel venting into the flare header (e.g. Closed Drain Sump) needs a PSV to protect against blockage of the final vessel. So where do I relieve the PSV? to atmosphere? Presumably each PSV needs to be sized for the blocked outlet flows from the associated vessel.
If locked-open valves are provided round a PSV to enable maintenance then does this mean that the vessel can be isolated from the PSV in the context of SAC A.4.c.3 and A.4.c.4?
Also, does the presence of a water-seal vessel downstream of the Flare KO Drum mean that the Flare Drum also needs a PSV to comply with API 14C.
I seem to be going round in circles so any comments & advice would be grastefully received.
If locked-open valves are provided round a PSV to enable maintenance then does this mean that the vessel can be isolated from the PSV in the context of SAC A.4.c.3 and A.4.c.4?
Also, does the presence of a water-seal vessel downstream of the Flare KO Drum mean that the Flare Drum also needs a PSV to comply with API 14C.
I seem to be going round in circles so any comments & advice would be grastefully received.