jcaiken,
As usual, when we work too much and it end-up we are questioning our believe like a dog chasing his own tail...
API 14C SAC A.4.c.5 seems to indicate that a PSV is required on a pressure vessel (max pressure >5 psig) unless it is the final vessel on a flare header (i.e. Flare KO Drum). However, this implies that any other vessel venting into the flare header (e.g. Closed Drain Sump) needs a PSV to protect against blockage of the final vessel. So where do I relieve the PSV? to atmosphere? Presumably each PSV needs to be sized for the blocked outlet flows from the associated vessel.
No matter how we interprete the statement in any code, ultimately is there is NO possibility existent of potential blockage results overpressure scenario.
Let say a degassing drum with vent line and flame arrester discharge to atmosphere directly. This drum is also consider "final vessel". However there is a potential of flame arrester blockage and an overpressure protection device is required.
Another example is two drum connected together can be protected with a PSV if there is NO possibility existent of potential blockage on the interconnecting line.
Another example is a Flare KOD with Flare Recovery system (e.g. compressor, eductor, etc). The flare line connected to flare stack may have an on-off valve to facilitate plant maintenance. Under this case, eventhough the Flare KOD is the "final vessel" but an overpressure protection device (i.e. rupture disk) would be installed across the on-off valve to ensure a clear relief path.
In your "closed drain sump connected to flare KOD case", i would consider a.4.c.4.
If locked-open valves are provided round a PSV to enable maintenance then does this mean that the vessel can be isolated from the PSV in the context of SAC A.4.c.3 and A.4.c.4?
Do you mean the isolation valves on the inlet and outlet of PSV or on the PSV bypass line ? I guess you mean the maintanance isolation valves on the inlet & outlet of PSV.
Strict compliance to code, there should be NO devices (i.e. valves) potential creating blockage between the protected equipment, PSV and disposal path. Nevertheless this does not allow PSV routine inspectionand change-out. The plant may require partial shutdown and blowdown for PSV maintenance and lossing inventory is not cost-effective. Thus, these valves are considered highest critical valves and handle by strict working procedures...This case possibly a deviation.
Also, does the presence of a water-seal vessel downstream of the Flare KO Drum mean that the Flare Drum also needs a PSV to comply with API 14C.
NO PSV is required.
Whenever a large relief, the water-seal will be destroyed and there is NO possibility existent of potential blockage results overpressure scenario.
Hope above help.
Best regards,
JoeWong