We have been using them, and are pleased with them. Yes, and the min is 9'-0" between heads. We like them for sloped ceilings,as they only require only 13 GPM @ 7 PSI with up to an 8/12 roof pitch, with a 16x16 head spacing "Great for a concealed sprinkler"
I will double check with UL before putting my license on the line. You know fake Michael Jordan products come Nike check too.
I seem to be confused as to only one overseas company hold a UL Logo. Specially a sprinkler head that does not meet a standard pattern. I dont know but I will stick to a company that could respond locally and not some john doe overseas that in case of a legal battle they vanish into the dark of the night.
These sprinklers are great. I use them all the time in designs. I think their distribution center is in Irvine, CA. They're concealed residential sprinklers are the smallest I've ever seen and the sprinklers are inexpensive. The 9'rule stinks but you get used to it.