JedClampett
Structural
- Aug 13, 2002
- 4,031
I wondered about that myself. But that isn't even the worst mistake. Since they didn't have the calculations, they should of studied every possible mechanism that might of been assumed. I think they could easily show that the design was inadequate no matter what load carrying pattern (cantilever or two way) is used. Plus they assumed the water was up to the top of the wall in their design calculations. I agree it should of been designed that way, but in the pictures, the liquid is a good foot or so below the top of wall. If the wall failed at a lower water level, the stresses at that level need to be checked.
They dwell on reinforcing lap lengths. But to prove that they had something to do with a failure needs a study of the stresses in the reinforcing at the lap location. After all, development lengths are allowed to be reduced if the analysis shows the bars aren't fully loaded.
This sloppy report, with its multiple offenders, will result in a muddying of liability, and no one being held accountable.
They dwell on reinforcing lap lengths. But to prove that they had something to do with a failure needs a study of the stresses in the reinforcing at the lap location. After all, development lengths are allowed to be reduced if the analysis shows the bars aren't fully loaded.
This sloppy report, with its multiple offenders, will result in a muddying of liability, and no one being held accountable.