Anchorage of mesh reinforcement in a composite slab

Status
Not open for further replies.

BucklingGuru2718

Structural
Joined
Jul 12, 2023
Messages
2
Location
GB
I have designed the mesh in a composite slab to resist the longitudinal shear that is caused by the composite action with the steel beams.

Some of the areas in the project are longer span and so I have decided to double up the mesh to provide more reinforcement locally. I need to determine how much anchorage I actually need to provide to these double-up areas of mesh.

Anyone here ever seen a way to calculate this, or perhaps have an idea of how this could be done? I have had a look through Eurocodes 2 & 4 as well as some composite design guides and have not found anything relating to this topic.
 
For concrete bridge decks composite with steel beams, AASHTO requires longitudinal reinforcing area equal to 0.67% of the cross sectional area of the deck, wherever the tension stress in the concrete exceeds 90% of the modulus of rupture, fr. For normal weight concrete, fr = .24*sqrt f'c.
 