Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Anchor Pullout

Status
Not open for further replies.

jcox

Structural
Joined
Jul 16, 2002
Messages
37
Location
US
In ACI 318-02 D.5.2.3, hef is limited to cmax/1.5. Figure RD5.2.3 is not particularly helpful since c1=c2=c3=4". My question is that for use in (D-6), is the cmax correct? If I have two anchors in tension that are 16" apart, and c1=c2=13", and c3=cmax=29", is hef limited to 19.33"? The figure indicates to me that the failure surface should be really dictated by cmin. But like I said I think using 3 edge distances that are equal is a poor illustration when trying to demonstrate how to apply a formula.

Thanks
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top