CELinOttawa: So you suggest that I quit my job rather than try to make it work?? I would love to insist on testing, but I am the workhorse in this project, not the project manager. Again, I appreciate the sentiment, but you are preaching to the choir on this one - I am just trying to not go crazy during the 40 hours have have to perform this analysis/design.
mtu: shear reinforcement is definitely a worry. I have seen many concrete beams deteriorated in old firehouses that had a sad amount of stirrups/bent-up bars.
Jed: No worries! I can handle it. Today I picked my boss's brain a bit more and found out that this garage was not from 1950, rather it is pre-WWII. If you look at slideruleera's reference for garage LL per city, my city was listed as 90 psf in the 1930's. I think that is where the difference is. Now we have three existing stories of 90 psf = 270 psf, minus three new stories of (15 DL + say 60 LL to account for corridors) = a balance of 55 psf. although, I don't really feel much better knowing that. Never mind the possibility (as you mention) of design or construction mistakes (cause' they NEVER happen).
BA: correct, my sign and seal is NOT going on these drawings. Actually, the new floors are going to have a smaller foot print than the lower garage floors.
KootK: Inevitable is correct. I will be certainly updating as I go along. I am curious what your opinions will be once the design is complete - hopefully they will be more comforting and optimistic by that point. I mean, all we have from the architect is a historical society approval set, and we just send our fee in. So, inevitably, a great deal of more concrete information will come out of the closet as it move along. Thanks for trying to be constructive - it is very appreciated! I agree with your ranting too - I hate all of those assumptions, and try to use them very very sparingly on non-critical or very redundant structures.
Brad: This is the whole kit and kaboodle. Schematic phase through construction documents and construction admin. Yup, no geotech (yet). I can find a way to work around the lack of testing for the superstructure, but as you all know soils are a dangerous realm to assume (or presume if you are in the IBC chapters). Besides, I want geotech's to get a job too - I am sick and tired of clients, owners, etc. not wanting to hire geotechs or other disciplines we structurals need for support (pun!). I feel like we end up being the jack (asses) of all trades in the name of $$$. Feww...I started ranting there.
There is an architect - we work for them. And, yes, it could cause a problem. For instance, the preliminary set shows two stair towers, but they aren't continuous and move around the footprint as you go vertical!! So much for using them for shear cores. My boss is an engineer (not much older than I) and I work at a consulting engineering firm. Good idea on the dwgs.
Robbiee: I agree that the scope does not allow for reduced seismic demand as a retrofit. All ASCE 7-10 and IBC 2012 loads and requirements.
WARose: This thread may account for some of that documentation!